HVAC / Coefficient of Discharge #14414
Unanswered
ShehabGamrah
asked this question in
Q&A
Replies: 1 comment 2 replies
-
There are DEVC outputs for HVAC that will show you the exact values at the nodes. The greenish area above the connection looks to be about -8. If the bottom is -28 then that is -20 total considering this is just using slice data and trying to eyeball the color is pretty close to the -22 you are expecting. Without a simple input file to look at can't say much more. |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
I am trying to include the coeficcient of discharge and compare to hand calculations. As seen in the picture below of pressure values. I modelled an HVAC Duct with an area of 1m2 and a forward and reverse loss (K) of 1.451 in the duct. This should be equivalent to a cd of 0.83 based on K=1/cd^2. Then using the formula for pressure drop across rectangular orifice. delta P = (Q/Cd* A)^2 ^0.5 * density = 21.77 Pa based on a flow rate of 5m3/s passing through the opening. However, monitoring the pressure values at upstream and downstream of the orifice the pressure drops to -28 Pa. So is something wrong in my calculations or is the CFD values offset from the hand calcs, and have to change the loss value in the HVAC duct.